3:2:1 The LPG
boiler shuts down on
start-up
”Red LED comes on immediately”
Cause:
- Resetting time too short.
- The pressure switch does not cut out.
- Fault in electronic ignition unit.
- Faulty wiring.
- Faulty printed circuit board.
Action:
- Reset the electronic ignition unit by switching off the
boiler on the control panel (the red LED goes out) and
wait at least 30 seconds before attempting a restart.
- Check that the pressure switch cuts out. There should
be 12 V on the white cable, connection no. 1 on the
pressure switch (fig. 4 A). If there is no voltage, replace
the pressure switch.
- Replace the electronic ignition unit.
- Check that the wiring connections are intact and correctly
fitted.
- Replace the printed circuit board with a new one.
oder:
3:3 The LPG boiler starts but goes
out after approx. 10 seconds
(red LED comes on)
Cause:
- The flame sensor cable is damaged.
- Faulty electronic ignition unit.
- Sensor damaged or incorrectly positioned.
Action:
- Check that the flame sensor cable is intact and correctly
connected.
- The only way to check whether the electronic ignition
unit is working is to change it and then check that the
boiler is operating properly.
- Remove the burner and check that the flame sensor is
intact and correctly fitted (see fig. 6). Replace the flame
sensor if necessary.